      Code Text Description Cause Check Procedure
      5201 Pressure sensor fault. PS1 Pressure fault. Check pressure reading using the dipswitches on the outdoor. Check connection of PS3 on PCB.

      Error Code 5201
      1. Error code definition
      High-pressure sensor fault (63HS1)
      2. Error definition and error detection method
      If the high pressure sensor detects 0.098MPa [14psi] or less during the operation, the outdoor unit stops once, turns to antirestart mode for 3 minutes, and restarts after 3 minutes when the detected high pressure sensor is 0.098MPa [14psi] or more.
      If the high pressure sensor detects 0.098MPa [14psi] or less just before the restart, the outdoor unit makes an error stop, and
      the error code “5201” will appear.
      During 3-minute antirestart mode, preliminary errors will be displayed on the LED display.
      A error is not detected for 3 minutes after the compressor start, during defrost operation, or 3 minutes after defrost operation.