6832 |
MA controller comms fault. |
MA controller being wired into the M-Net. Wrong cable size/spec. |
Check where remote is wired to, check cable length no bigger than 500 meters, check connection and type of cable used, check R/C not set Sub on field settings |
|
6832 |
Communication fault between the Lossnay and the PZ-61DR-E |
Remote controller wiring has been terminated incorrectly.
PZ-61DR-E is in the same group as a LGH-RX5 Lossnay. |
Check the termination of the remote controller wiring.
The PZ-61DR-E cannot be used in the same group as a LGH-RX5 Lossnay. |