      Code Text Description Cause Check Procedure Technical Support Notes
      6834 MA controller comms fault. MA controller being wired into the M-Net instead of the remote terminals. Wrong cable size/spec. Check where remote is wired to, check the cable length is no bigger than 500 meters, check connection and type of cable being used, check R/C not set Sub on field settings. This is usually caused when an M-Net controller is replaced with an MA controller. Make sure if you have an M-Net remote it is wired into the M-Net terminals and if you have an MA remote it is wired into the remote controller terminals.
      6834 Communication fault between the Lossnay and the PZ-61DR-E Remote controller wiring has been terminated incorrectly.

      PZ-61DR-E is in the same group as a LGH-RX5 Lossnay.

      Remote controller wiring has been terminated incorrectly.

      PZ-61DR-E is in the same group as a LGH-RX5 Lossnay.