      Error Code 6843
      1. Error code definition
      A control communication start bit detection error
      2. Error definition and error detection method
      Indoor/outdoor unit communication error
      Abnormal if indoor controller board could not receive any signal normally for 6 minutes after turning the power on.
      Abnormal if indoor controller board could not receive any signal normally for 3 minutes.
      Consider the unit as abnormal under the following condition. When 2 or more indoor units are connected to an outdoor unit,
      indoor controller board could not receive a signal for 3 minutes from outdoor controller circuit board, a signal which allows
      outdoor controller circuit board to transmit signals.
      3. Cause, check method and remedy
      1. Error code definition
      A control communication start bit detection error
      2. Error definition and error detection method
      Indoor/outdoor unit communication error (Outdoor unit)
      Abnormal if outdoor controller circuit board could not receive anything normally for 3 minutes.
      3. Cause, check method and remedy
      Note: Refer also to the Service Handbook for the indoor units.
      Cause Check method and remedy
      (1) Contact failure, short circuit or miswiring (converse wiring) of indoor/outdoor unit connecting wire
      Check disconnecting or looseness of indoor
      /outdoor unit connecting wire of all indoor
      units or outdoor units.
      (2) Defective transmitting receiving circuit of outdoor controller circuit board.
      Turn the power off, and on again to check. If
      abnormality generates again, replace indoor
      controller board or outdoor controller circuit
      board.
      Note: other indoor controller board may have
      defect.
      (3) Defective transmitting receiving circuit of indoor controller board.
      (4) Noise has entered into indoor/outdoor unit connecting wire.
      (5) Defective fan motor Turn the power off, and detach fan motor
      from connector (CNF1, 2). Then turn the
      power on again. If abnormality is not displayed, replace fan motor. If abnormality is
      displayed, replace outdoor controller circuit
      board.
      (6) Defective rush current resistor of outdoor power circuit board Check the rush current resistor on outdoor
      power circuit board with tester. If open is detected, replace the power circuit board.
      Cause Check method and remedy
      (1) Contact failure of indoor/outdoor unit connecting wire Check disconnection or looseness of indoor/
      outdoor unit connecting wire of indoor or outdoor units.
      (2) Defective communication circuit of outdoor controller circuit
      board
      Turn the power off, and on again to check.
      Replace indoor controller board or outdoor
      controller circuit board if abnormality is displayed again. (3) Defective communication circuit of indoor controller board
      (4) Noise has entered into indoor/outdoor unit connecting wire