Function setting error |
More than 1 unit in the group is set to as the Main Lossnay (SW5-10 ON)
The group contains two or more units with the same address.
The Lossnay that is set to the Main, has not been set to the lowest unit address in the group.
The MA remote controller for the air conditioner (Mr.Slim or City Multi) is connected to the Lossnay.
Incorrect wiring of the remote controller terminals.
The Lossnay LGH-RVX is in the same group as a Lossnay LGH-RX5.
The model selection switch SW6 is not set correctly. |
Check the SW5-10 setting on the Lossnays in the same group and confirm that there is only one set to Main(ON)
Check the address settings of the Lossnay units.
Change the remote for a PZ-61DR-E.
Check that the wiring of the remote terminals and the MNET terminals.
The LGH-RVX and the LGH-RX5 cannot be used in the same group.
Confirm that the SW6 setting is correct for the model. |