    theachub_m40wgrTheAChub
    Keymaster

      Premium

      Fan Motor (M1F) Lock, Overload

      Error Code           A6

      Applicable

      Models

      FXFQ, FXHQ, FXAQ
      Method of Error

      Detection

      Abnormal fan revolutions are detected by a signal output from the fan motor.
      Error Decision

      Conditions

      When the fan revolutions do not increase
      Supposed

      Causes

      „     Broken wires in, short circuit of, or disconnection of connectors from the fan motor harness „ Defective fan motor

      (Broken wires or defective insulation)

      „     Abnormal signal output from the fan motor (defective circuit)

      „     Defective PCB

      „     Instantaneous disturbance in the power supply voltage

      „     Fan motor lock

      (Due to motor or external causes)

      „     The fan does not rotate due to foreign matters blocking the fan.

      „     Disconnection of the connector between the high-power PCB (A1P) and the low-power PCB

      (A2P)

      ∗1.If any junction connector is provided between the connector (X20A) on the indoor unit PCB and the fan motor, also check whether or not the junction connector is properly connected.

      ∗2.Check on connector of fan motor (Power supply cable) Turn OFF the power supply.

      Measure the resistance between phases of U, V, W at the motor side connectors (3-core wire) to check that the values are balanced and there is no short circuiting, while connector or relay connector is disconnected.

      ∗3.Check on connector of fan motor is not available for below models.

      FXFQ09~48PVJU, FXAQ07~24PVJU

      Indoor Unit Fan Motor Abnormality

      Error Code       A6

      Applicable

      Models

      FXDQ
      Method of Error

      Detection

      This error is detected if there is no revolutions detection signal output from the fan motor.
      Error Decision

      Conditions

      When no revolutions can be detected even at the maximum output voltage to the fan
      Supposed

      Causes

      „

      „

      Defective indoor fan motor

      Broken wires

      „ Defective contact

      Indoor Unit Fan Motor Abnormality

      Error Code    A6

      Applicable

      Models

      FXMQ-PB
      Method of Error

      Detection

      Error from the current flow on the fan PCB

      Error from the RPM of the fan motor in operation

      Error from the position signal of the fan motor

      Error from the current flow on the fan PCB when the fan motor starting operation

      Error Decision

      Conditions

      „ An overcurrent flows.

      „ The RPM is less than a certain level for 6 seconds.

      „ A position error in the fan rotor continues for 5 seconds or more.

      Supposed

      Causes

      „     The clogging of a foreign matter

      „     The disconnection of the fan motor connectors (X1A and X2A)

      „     The disconnection of the connectors between the indoor unit PCB (A1P) and fan PCB (A2P) „ Defective fan PCB (A2P)

      „     Defective fan motor

      Overload / Overcurrent / Lock of Indoor Unit Fan Motor

      Error Code       A6

      Applicable

      Models

      FXMQ-M
      Method of Error

      Detection

      This error is detected by detecting that the individual power supply for the fan turns OFF.
      Error Decision

      Conditions

      When it is not detected that the individual power supply for the indoor unit fan turns ON while in operation.
      Supposed

      Causes

      „

      „

      Defective power supply for the indoor unit fan motor

      Clogged drain piping

      „ Actuation of the indoor unit safety device
      „ Defective contact in the fan wiring circuit