Transmission Abnormality between Indoor Unit PCB and Fan PCB
Error Code C1
Applicable
Models |
FXMQ-PB |
Method of Error
Detection |
Check the condition of transmission between indoor unit PCB (A1P) and fan PCB (A2P) using computer. |
Error Decision
Conditions |
When normal transmission is not conducted for certain duration. |
Supposed
Causes |
|
Connection defective the connecter between indoor unit PCB (A1P) and fan PCB (A2P)
Defective indoor unit PCB (A1P) |
|
|
Defective fan PCB (A2P) |
|
|
External factor, such as instantaneous blackout |
blackout).
Note: ∗1.Pull out and insert the connecter once and check it is absolutely connected.
∗2.Method to check transmission part of indoor unit PCB.
- Turn OFF the power and remove the connecter X70A of indoor unit PCB (A1P).
- Short circuit X70A.
- After turning ON the power, check below numbers under field setting from remote controller. (Confirmation: Second code No. at the condition of first code No. 21 on mode No. 41)
↓
Determination01: Normal
Other than 01: Transmission error on indoor unit PCB ∗ After confirmation, turn OFF the power, take off the short circuit and connect X70A back to original condition.