      Humidity Sensor System Abnormality

      Error Code

      CC

      Applicable

      Models

      FXFQ
      Method of Error

      Detection

      Even if an error occurs, operation still continues.

      Error is detected according to the moisture (output voltage) detected by the moisture sensor.

      Error Decision

      Conditions

      When the moisture sensor is disconnected or short circuited
      Supposed

      Causes

      „

      „

      Defective sensor

      Disconnection

      Troubleshooting

      It is believed that external factors (noise or else) other than failure caused the error.

       Note: ∗1.To delete the history, the  ON/OFF  button of the remote controller must be pressed and held for 5 seconds in the check mode.

      ∗2.To display the code, the  INSPECTION/TEST Operation  button of the remote controller must be pressed and held in the normal mode.

      ∗3.If “CC” is displayed even after replacing the humidity sensor PCB assy (A2P) and taking the steps ∗1 and 2, replace the indoor unit PCB assy (A1P).