Actuation of High Pressure Switch
Error Code E3
Method of Error
Detection |
Detect continuity across the high pressure switch in the protection device circuit. |
Error Decision
Conditions |
When part of the protection device circuit opens.
(Reference) Operating pressure of the high pressure switch:
Operating pressure: 4.0 MPa (1338 ftH2O)
Resetting pressure: 3.0 MPa (1004 ftH2O) |
Supposed
Causes |
|
Activation of high pressure switch
Defective high pressure switch |
|
|
Defective control PCB (A1P) |
|
|
Momentary power failure |
|
|
Defective high pressure sensor |
Note: ∗1. Make a comparison between voltage measured by the pressure sensor and that read by the pressure gauge.
(The pressure sensor makes measurement of voltage at its connector block to convert it to pressure. CHECK 12 ) CHECK 1