      Outdoor Unit Fan Motor Abnormality

      Error Code

      E7

      Applicable

      Models

      REYQ-T
      Method of Error

      Detection

      „ Detect according to the value of current flowing through the inverter PCB (or fan inverter PCB in case of Fan Motor 2).
      „ Detect error of the fan motor system according to the fan revolutions detected by the hall IC during the fan motor runs.
      Error Decision

      Conditions

      „ When overcurrent is detected from the inverter PCB or the fan inverter PCB (Detecting overcurrent 4 times will shut down the system).
      „ When the fan revolutions fall below a given level for a period of 6 seconds while in fan motor rotation mode (Detecting shortage of revolutions will shut down the system).
      Supposed

      Causes

      „

      „

      Fan motor failure

      Neglect to connect or defective connection of harness/connector between the fan motor and the

      PCB

      „ Fan does not rotate due to foreign matters caught in it.
      „ Clearing condition: fan motor performs normal operation for a period of 5 minutes

      Troubleshooting