      Outdoor Unit Fan Motor Signal Abnormality

      Error Code       H7

      Applicable

      Models

      REYQ-T
      Method of Error

      Detection

      Detect of abnormal signal from fan motor.
      Error Decision

      Conditions

      When an abnormal signal is detected at startup of the fan motor operation.
      Supposed

      Causes

      „

      „

      Abnormal signal from fan motor (Circuit failure)

      Disconnection/Short circuit in fan motor leads or disconnection of connector

      „ Defective inverter PCB (A3P, A6P)
      • For Fan motor 2, replace the fan inverter PCB A7P.

       Note:   ∗1.Procedure for checking for the connector of the fan motor.

      • Turn OFF the power supply.
      • Disconnect the connector (X2A or X502A) from the PCB, and then make measurement of the following resistance. Acceptance criteria: Resistance between phases falls within the range of ±20%.