Yes it’s a 407c unit. I spent a bit of time looking at it today.one thing I found – was that th1 thermistor{ compressor discharge) was reading 123c even with the unit off, I changed the sensor but it made no difference, still showed 123c when running, when-pipe temp was only 76c.
Would this be enough, to stop the compressor ramping up to full load ? Im presuming it must be an issue with the main board causing the sensor reading error.
I have a board off a PUHY YMF C, it looks the same, but was going to check to see if it’s compatible with a PURY unit, as a replacement board is £350 .