Refrigerant Shortage
Error Code U0
Method of Error
Detection |
Detect refrigerant shortage according to a low pressure level or a difference in heat exchanging temperature from the suction pipe. |
Error Decision
Conditions |
Low pressure becomes 0.1 MPa (33.5 ftH2O) or less.
∗ Error is not determined. The unit continues the operation. |
Supposed
Causes |
|
Refrigerant shortage and refrigerant clogging (wrong piping)
Defective thermistor |
|
|
Defective low pressure sensor |
|
|
Defective outdoor unit main PCB |
Troubleshooting
Replace the outdoor unit main PCB (A1P). Remove the factor of decreasing low pressure.
CHECK 2
Note: ∗1.Check the low pressure value by using pressure gauge in operation.
∗2.Compare the actual measurement value by pressure sensor with the value by the pressure gauge.
(To gain actual measurement value by pressure sensor, measure the voltage at the connector [between (2)-(3)] and then convert the value into pressure. CHECK 12 ) CHECK 2